Hi, I have changed 3 AVR on Perkins Generator 2306C-E14 (FGB061018U4412K) after explosion or burnt each one 2 to 3 weeks ....I need the root cause of the problem .... Thanks Eng's in advance...
That is the model of the engine but it does not tell anything about the generator. What kind of generator is this on?
Thanks for reply the generator LS Leroy Somer
Leroy Somer Model number?
Leroy Somer Model number RPES2 by FG wilson
That looks like the FG wilson number, not the number of the Leroy Somer alternator...and we have nothing like that FG Wilson unit over here near as I can tell. Have you tried discussing it with FG Wilson? Otherwise try and find the Leroy Somer model on the alternator itself.
My experience this happens when the exciter field becomes shorted. The only load of the AVR is the exciter field. I have had numerous times with failures and the only cure was an exciter field (exciter stator) replacement.
Thanks gents, I attached to the name plate of engine and alternator ... about the resistance of exciter stator was 11 Ohm now it's running at 50% of load with direct connection of 12VDC for more than 10 day's with out AVR. Still with out any solution.
That exciter resistance sounds a little bit low. I can't find what the specification is supposed to be on this model, though. Also, did you check exciter stator for grounds?
Look under leroy-somer.comdocumentation-pdf4455_en.pdf for that type it shows 12.5 ohms exciter field resistance
Assuming the field is not grounded or intermittently shorted, I would next try an aftermarket voltage regulator and see if it behaves any differently.
Thanks gents Exciter not grounded I'm not sure the value ... but let me guess that was to ground 14 K ohm or more.... Is there any relation with back power to the neutral cable...
http://www.leroy-somer.com/documentation_pdf/4455_en.pdf Another thought, it might be a rotating diode failed. This would cause the AVR to work harder for the same output. If I recall, it is a lot of work but you might be able to reach in and disconnect the individual terminals from the rotating rectifier and test the diodes individually on this model.
I did not test the diodes ... but it will fail and show up 0 Volt from the beginning when I start the genset even with the direct 12 DCv,like it is now working by 12 DCv supply....
So you are saying sometimes it will not work even with 12 VDC applied? But usually it does?
No ... bro ... Now the generator working with 12Vdc applied with out AVR and and working fine with load around 40% from rated Kw ...I wish it will not damage the alternator .... I will not give up