12″ Water Main Leak

xcavate ยท 2008-07-09 19:52

I have a job were another crew installed 400' of 12" ductile water line. The line is leaking out about 8 trash barrels of water in about 30 min.It leaks only from 200psi to 150psi then stops. It holds static pressure. So a pretty sizeable leak. The boss had the leak detectors come out with there high tech gadgets and cant find the leak. I am left with the task now of trying to repair this thing. We have the leak isloated between two gate valves and there is one mechanical joint in the run. I have already dug up one of the gate vavles and had to put 8 turns on the bolts noone tighten them but that wasnt the leak. Then i dug up the 3 bells behind it and the 45 bend and still no leak. The other gate is located in the middle of the street and I did that tie in. First bell is on the shoulder of the road so it will be tough to dig up. The leak detector think it might be a split in a length a pipe and thats why he cant pick it up. I dont want to remove the dirt from the whole main at once due to it might buckle and blow the joints apart. So do I dig the rest of the bells up and hope its a rolled rubber or expose the whole thing a lil at a time and hope i find it. I have a pump on hand to keep at 200 psi while we look for it. Any suggestions?

Replies34
  1. #1RollOver Pete2008-07-09 20:00

    Check out the bells first. It's much easier than digging up the whole thing. But pay attention to what you are digging up. Your leak will travel along the bottom of the main. When you dig out a bell, a little extra effort digging to the bottom may show you which direction to go.

  2. #2xcavate2008-07-09 20:05

    Im just surprised with about 200 gallons leaking out it hasnt surfaced anywhere. The pipe is in sand and we havent even found a spec of water yet.

  3. #3danhoe2008-07-09 20:20

    Dig up the mech. joint first, if you already had to tighten up one joint chances are that the other one needs to be snugged up. A rolled rubber on 12" was pushed home with the hoe and the operator would have felt it. How many gallons are you loosing ? how many times have you pumped it up, are there a bunch of dips in the line you might need to work the air out, when you bleed the line out of a hydrant or corp if the water is milky that is a sign of air in your line. pm me if you want I will check in the morning leave me your mobile I will call you and get your problem solved. Dan

  4. #4stumpjumper832008-07-09 20:24

    I dont know if any companies in your area are simlarly eqquped, but a company named Abel recon, a division of abel construction in mountville, pa. Has a camera crawler that can go down the pipe and have a look see. They may have other technologies that might help too.

  5. #5dayexco2008-07-09 20:29

    any hydrants inline? if so, can you isolate it? sometimes the "guts" of a hydrant won't hold pressure, and they'll pee up to the bleeder hole, if you have rock around the hydrant, and never expose themself

  6. #6xcavate2008-07-09 20:47

    Well I have pumped it up about 10 times. The water line is pitched up hill. The main was filled slowly and bleed to the water comes out clear. No hydrants inline and I already dug up the mechanical joint. Its either a split piece of pipe, rolled rubber or some out the gate vavle might be back feeding which I doubt. I have cranked down on the gates and I dont hear any bypass and the correlator didnt pick up anything. It takes about 8 trash barrels to pump up to 200psi and it all leaks out. So somewhere in between 200 and 300 gallons. The correlator guy thinks its a spilt peice of pipe. He says if it was a rolled rubber he would have picked up on it.

  7. #7xcavate2008-07-09 20:52

    The second time I pumped it up it held 200psi for 50 min before leaking. The first time and every other time I have lost the amount of water described above. This just stumps me.

  8. #8dayexco2008-07-09 20:53

    ductile? my bet's on a rolled/torn gasket. haven't seen many split ductile pipes in my 40 yrs.

  9. #9PipeGuy2008-07-09 20:54

    does the line pressure always stop at 150 psi? What is the pressure on the main from the city? I would lean towards the MJ fittings to look for the leak. If you have much deflection on your bells look there next, for instance if your water main goes up and down a hill and you just deflected the bells instead of using fittings. A couple of years ago we had a watermain with a leak and we bact tested it and left the main live. The main was on for about 4 months and the leak never surfaced and it also was in sand. I still would say you best bet is the MJ fittings then dig the bells.

  10. #10xcavate2008-07-09 20:59

    City main is at 85 psi or so. The main always stops leaking within 15 psi of 150psi.

  11. #11JimBruce422008-07-09 21:31

    Sounds familiar... I was on a job this spring, where we had a leak during the pressure test for a new 16" ductile iron run. The guy with the fancy "thingamabobs" came out, went to the far points, and started to narrow it down, but couldn't without getting on the pipe. So we had to dig holes, here, and there eventually we got it to a T-joint and hydrant, but that wasn't it either, went a little further up from it to the joint, nothing, next joint nothing, but the sensor guy was able to say we were within X feet. Long story short (too late ), turns out that it was a split about 6" long in the pipe itself. The sensor guy said that if it had been a joint or a valve he would have been able to narrow it down in a flash, but a crack in the pipe apparently is a lot trickier to narrow down without digging. We didn't have any water bubble up either, the pipe run was all shot, so we figure the water was finding a seam in the rock and just following it out.

  12. #12Dwan Hall2008-07-09 21:44

    I don't know what I am talking about here but have you ruled out one of your valves not seating? Could go back to the next valve on bath end and test those sections at the same time. may be worth a try.

  13. #13dayexco2008-07-10 07:45

    that is a GREAT idea!....could have existing valve that's bleeding back on you.

  14. #14xcavate2008-07-10 16:20

    Well we think we found the leak..... We have it isolated to the first length of pipe off the street. In the middle of the length is the testing corp. We are thinking maybe the corp was screwed in crossthread.

  15. #15tylermckee2008-07-11 00:19

    Only time we ever get leaks is on the saddle/corp, or on flanged fittings where someone didnt keep the flange faces clean. And we never trust valves, new or old they dont always seal 100% at 200+ PSI.

  16. #16mjd372008-07-11 22:52

    I had a similar problem last fall, and it turned out to be the new valves we installed. The submittals were approved for valves with a pressure rating of 150psi. Didn't work too good on a 250psi test.

  17. #17xcavate2008-07-12 08:05

    Its not the gate valve backfeeding. I have water coming out from under the road. There are no bells under the road. So its either the megalug on the gate or the testing corp which is a direct thread no saddle. It goes from 200 psi to 150 psi in less then 20 min.

  18. #18AtlasRob2008-07-12 15:47

    Sorry cant help, but am intrested in your terminology. Gate valve, Ok no prob. Bells ? ( push joints on lengths of pipe, male one end, female (bell )on other ? Megalug ? Testing Corp ?

  19. #19dayexco2008-07-12 18:03

    first pic is of a mega-lug...it's a joint restraining device for mechanical joint pipe can't find a pic of a corp valve handy....it's just a valve attached to the watermain...for typically a home service connection.

  20. #20RonG2008-07-13 06:45

    The male and female ends of our pipe are called Bell and Spigot in this country. That Megalug retaining ring has torque to yeild lugs on it in that you tighten until they break but some inspectors require them to be tighter than the engineers design spec so underneath the the hex nut that breaks off is a smaller hex nut that could be used for removal and the inspectors require a torque wrench on site to snug them up to their specs which can be real fun on the bottom side of the pipe.Ron G

  21. #21digger242j2008-07-13 09:53

    Everybody calls it a "corp" so often that they forget that the actual name is "corproration stop".

  22. #22xcavate2008-07-13 10:12

    Pics Here are some pics of the affected area. Its the line on the left that is leaking.

  23. #23ForsytheBros.2008-07-14 00:36

    xcavate- sorry to chase this rabbit down a different trail, but i don't notice polywrap on the ductile iron piping in the backfill pics. Do lots of jurisdictions not require wrap on DI piping?

  24. #24SKP 4282008-07-14 09:24

    I had a job 2 years ago that was a 12" dip main line was over 2 miles long with 3 line vales we and we had a leak in the line .It was a 275 psi test the line had a leak at 275 psi. but when we tested lower than 170 psi it would hold . after a week of looking .I hammered the line a few times around 275+ psi and it opened up the leak so that it would leak at 150 psi 1 gal in 15 min. we had a leak locator out and he could never find the leak. We luckily found the leak by just digging up bell holes and we smelled chlorine and started digging up the middle of pipes .We found the leak it was a crack in the dip it had all the coating on it and the concrete liner in the pipe had a hair line crack in the concrete. Luckily we found the needle in the hay stack .

  25. #25d4c24a2008-07-14 13:12

    ductile the ductile pipe here in the uk no longer needs to be wrapped with polywrap due to the advance in coatings :notworthy better to lay it that way cheers graham

  26. #26AtlasRob2008-07-14 14:29

    Thanks for that, still a little unsure exactly how it works. Looks rather like what I know as half of a Viking coupling. :drinkup Thanks Digger, alls clear as mud now :thumbsup

  27. #27Turbo218352008-07-14 18:30

    Around here It depends on the municipality. It depends on soil type too. We have aggressive sandy soils in areas. It beats on the pipe pretty bad. That gets a bag over it. Other areas have soils that are not aggressive, and the municipality does not require a bag.

  28. #28ForsytheBros.2008-07-14 18:33

    Atlas- the general principle behind the "megalug", or joint restraint is as follows: Static pressure and momentum forces act on the pipeline in various scenarios: eg, a bend in the pipeline, a "tee" intersection, etc. Previously, i'm told, concrete thrust blocking was placed at bends, tees, etc. to act as a mass to resist these forces and prevent pipeline breaks and other undesirable things. The joint restraint Dayexco posted replaces the standard gland used to attach a fitting (ductile iron 45 deg bend, 90 deg bend, tee, valve, etc.). The projections, as i believed mentioned by others, have shear bolts that break at a predetermined torque setting. Essentially, these bolts have serations which "bite"/grip the outer walls of the pipeline. The theory is that since this gland is locked to the pipe without movement, the fitting attached to it should perform likewise. If maintenance is required on the pipeline, a benefit of the megalug is that its removal is simpler than having to jackhammer out a bunch of concrete massed around a pipe fitting or bend. That said, we've been on a couple of jobs where restrained joints were required, but concrete thrust blocking was also incorporated. Belt and suspenders, i suppose. Please forgive me if my response was too simplistic or i'm repeating others.

  29. #29dayexco2008-07-14 19:08

    we do quite a bit of piping on ethanol plants, last one had 8000 l.f. of fire main, 17 hydrants...they required mega-lugs on ALL m.j. joints, ...PLUS a min. of a 1 yd. of concrete thrust block poured in place. a little redundant i spose...but if that's what they want to pay for....i'll do it

  30. #30ForsytheBros.2008-07-14 22:35

    belt and suspenders Day- we just got off of a reclaimed water project (16" DI)- one particular bend had concrete thrust blocking, megalugs (sigma one-lok) and threaded rod restraint. Are there any more restraint systems? Hopefully it won't move much...... I concur with you- if that's the plan, so be it. But i digress, back to the leak issue........

  31. #31MKTEF2008-07-15 05:15

    In Norway we would never lay waterpiping like that. All pipes is laid with couplings inside concrete manholes. Community demands it for test, leakage, inspection, new connections and maintenance. There is also a hydrant coupling on top of the cross. Fire dep opens the manhole and climbes down with a fire connection. The megalugs have i never seen. We get brackets prefabricated inside the bottom of the concrete manholes. Stainless steel. Added a picture here showing a example of a concrete manhole. 10 feet inside dia, prepared for a 400 mm waterpipe.(1 1/3 feet pipe) Here it got 3 holes for the mainpipes. Holes is sealed with a rubber gasket to ceep water outside. U can se the bracket on the floor.

  32. #32danhoe2008-07-15 20:06

    In Michigan anything over a 8" valve goes in a gatewell, this is in southeast Michigan, 6" valves get a d box which are on a fire hydrant leads. Turbo and I were talking at work today how much termology and methods change around the country and the world. In 1988 I was digging in Detroit we replaced wood ( Tamarack )watermain installed in the 1890's, it was still in service at the time. In high acid types of soil we use C-900 plastic pipe. This turned out to be a good post, I have been bacterial & pressure testing for about 25 years. I had a 16" line full of peat and passed the test, then the next job we had a bad source and could not pass the test. Pressure testing is also a challenge. Good post, danhoe

  33. #33MKTEF2008-07-16 07:04

    I agree on the post, a lot of interresting info here.:drinkup I don't do much of this type of work, but got my license for it. In these concrete rings there is often mounted a testconnection to the cross. Either on one of the extensions or as a inbetween conected on the line. Basic rule here is to always pressure test the line before u fill over it. Having to dig it up afterwards is realy going to be expensive... Same goes for controlling direction of the lines. Waterplants/community has very strict rules on desinfecton, ovalitycheck, pressuretest and inline mounting. Most demand a third company doing the test, alingment and desinfection. More and more popular is also to demand video of the pipes from the inside.

  34. #34AtlasRob2008-07-18 14:19

    Thank you very much, simplistic works for me . I was having trouble with the shear ( torque ) locking bolts, but got it now ( I think ) I have never come across that sort of restraint in the UK but am familiar with thrust blocks. Thanks to Dayexco also. :drinkup